Note: "permalinks" may not be as permanent as we would like,
direct links of old sources may well be a few messages off.
Vampire D wrote: > Is it possible to setup a reliable DRBD configuration without using > STONITH interface? We want to place some units in a rackspace at a > data center and do want to have to have UPS units sitting in the rack > to shut them down. > Depending on your hardware you could use IPMI to do a hard power cycle powered by stonith. We do this with IBM and Dell kit - works fine -- Clive